Default Electrical Q

Earlier today I set up a mag 7 on a reactor. Everything was fine. The mag 7 is plugged into my aquatronica power bar. During a water change I turned off everything in the sump (I do my waterchanges via the sump) did my waterchange and restarted everything. Upon restart of the mag 7, the GFCI tripped. I thought it odd but turned off power to the halides (they suck the most power 2x250W) and tried again, tripped the GFCI again.

I unplugged the mag 7 and tried plugging it directly into the GFCI, tripped again. I then plugged the mag 7 into a non GFCI circuit and it works fine.

However, now I'm wondering wtf is up with the mag 7. Is it leaking power? I have no grounding probe.

Its my understanding that it doesn't take much to trip a GFCI but it takes more to trip a breaker? The plug is completely dry. Why did it work fine earlier and now its causing problems?

So my question is, if something trips a GFCI and not a breaker, should I be removing it from my tank or is it just "one of those things" and its probably fine. The fish look fine however I don't want to wake up in the morning to a bunch of dead or wonky looking fish.
__________________
Christy's Reef Blog

My 180 Build

Every electronic component is shipped with smoke stored deep inside.... only a real genius can find a way to set it free.
Reply With Quote
  #2  
Old 03-20-2010, 04:40 AM
H22_TURBO's Avatar
H22_TURBO H22_TURBO is offline
Member
 
Join Date: Apr 2009
Location: Edmonton
Posts: 62
H22_TURBO is on a distinguished road
Default

maybe try plugging it into another gfci and test it? could be the gfci is no good anymore???
Reply With Quote
  #3  
Old 03-20-2010, 04:52 AM
christyf5's Avatar
christyf5 christyf5 is offline
Staff
 
Join Date: Aug 2001
Location: Nanaimo
Posts: 9,175
christyf5 is on a distinguished road
Default

but everything else on the GFCI is fine when I run it without the mag 7 so the GFCI appears to be fine (?)
__________________
Christy's Reef Blog

My 180 Build

Every electronic component is shipped with smoke stored deep inside.... only a real genius can find a way to set it free.
Reply With Quote
  #4  
Old 03-20-2010, 05:02 AM
Delphinus's Avatar
Delphinus Delphinus is offline
Member
 
Join Date: Dec 2001
Location: Calgary
Posts: 12,896
Delphinus has a spectacular aura aboutDelphinus has a spectacular aura aboutDelphinus has a spectacular aura about
Send a message via MSN to Delphinus
Default

I'm a little bit fuzzy on how a GFCI works in that it either implies power on the ground wire and thus a "leak", or whether there is an imbalance between hot and neutral and thus a "leak". Either way though, I'd say it's not good. I would look at that mag 7 and see if there's anything wonky with the wire where it attaches to the pump itself.

In an electrical leakage situation, the fish themselves aren't ground so they're fine (although it's still not good for them - think it can cause HLLE ?), but as a person with feet on the ground it's bad.

At least that's how I sort of understand it.
__________________
-- Tony
My next hobby will be flooding my basement while repeatedly banging my head against a brick wall and tearing up $100 bills. Whee!
Reply With Quote
  #5  
Old 03-20-2010, 05:32 AM
Starry Starry is offline
Member
 
Join Date: Dec 2005
Location: Lethbridge, AB
Posts: 619
Starry is on a distinguished road
Default

could always put the mag in a tub of sw and meter it for stray current. (not with your fingers standing barefoot on concreat)
__________________
Starry
180 custom starfire
http://s1083.photobucket.com/albums/...0%20july%2007/
Reply With Quote
  #6  
Old 03-20-2010, 05:33 AM
ottoman ottoman is offline
Member
 
Join Date: Jul 2007
Location: Vancouver
Posts: 106
ottoman is on a distinguished road
Default

Is it possible that you have a bit of splash or moisture on the plug or GFCI during the water change? Just my thought.
Reply With Quote
  #7  
Old 03-20-2010, 05:42 AM
DiverDude's Avatar
DiverDude DiverDude is offline
Member
 
Join Date: Feb 2010
Location: Calgary
Posts: 519
DiverDude is on a distinguished road
Default

GFCI's work like this: Normally, current flows between HOT (black/larger blade of the plug) and NEUTRAL (white/smaller blade). Under normal circumstances, there is no current flow in the ground wire (green wire).

When someone somehow makes contact with either HOT or NEUTRAL, they can potential conduct (via their body) to ground. This poses a safety risk -particularly if one hand is in contact with the live wire and the other is at ground potential since the path is across the chest and there is a chance of fibrilation (this is BAD, very bad).

Enter the GFCI. It senses if there is current flow in ground. If there is, it surmises that something is not koscher and cuts power to protect the human it supposes is doing this. It's worth pointing out that GFCI's are to protect people, not the equipment. Equipment is protected by the breaker.

So.....this would imply that your pump is leaking to ground somehow -or the GFCI is faulty. I'd try plugging the pump into another GFCI and see if it pops.

Does the Mag7 have a 2-prong plug or a 3-pin (grounded) plug ? If it has a grounded plug and pops another GFCI, I'd replace the pump.
__________________
-Mark

29 Gal Bowfront w/24" LED Lights. DIY HOB Sump (5.4 Gal) MP40. Orange Spotted Watchman Goby, 2 Clownfish and a few hermits.
Reply With Quote
  #8  
Old 03-20-2010, 05:44 AM
outacontrol outacontrol is offline
Member
 
Join Date: Jan 2010
Location: Stony Plain
Posts: 230
outacontrol is on a distinguished road
Default

Okay, here is how a GFCI works, it measures the current flow on the white and black wire and compares the 2 values, if the value is different by more than 6mA (0.06 amps) it will shut off the Circuit, because that current must be faulting to ground. Old GFCI receptacles had no self check circuitry in them and if they failed internally there was no indication until an accident or external test occured. New GFCI receptacles (sometimes labeled "smart lock") have an internal self check circuit and if they have an internal fault they will shut off.
So how old is the receptacle if it is newer than 2 or 3 years it might be a smart lock, and just need to be changed.
I would plug the pump into another GFCI (after checking all the wires for any damage or salt creep or moisture) and try that to see if it works.
Feel free to ask me any other questions.
I am a Master Electrician.
Reply With Quote
  #9  
Old 03-20-2010, 05:54 AM
Delphinus's Avatar
Delphinus Delphinus is offline
Member
 
Join Date: Dec 2001
Location: Calgary
Posts: 12,896
Delphinus has a spectacular aura aboutDelphinus has a spectacular aura aboutDelphinus has a spectacular aura about
Send a message via MSN to Delphinus
Default

Everytime the question of how a GFCI works I see exactly this (which is why I said I wasn't sure). One post that says "current on the ground = trip" and one post that says "hot/neutral amp imbalance = trip". I know a few years ago I caused a GFCI to trip on an otherwise empty circuit (ie., nothing was on that was plugged in) because I touched my light reflectors and got a static shock. That suggests "current on the ground", but the "hot/neutral imbalance" makes more sense to me or at least would be a safer option because if electricity can escape out of the wires into the tank, it's not necessarily going to work it's way back to the same ground wire that the GFCI is on.

Is is possible it is a combination of both options? Sorry, I'm not trying deliberately to be dense, but I am legitimately confused since I always see the same two different explanations when this topic comes up.

Either way though - if the GFCI itself isn't faulty then it's bad that the mag pump trips the GFCI. It may be the end of the road for the pump.
__________________
-- Tony
My next hobby will be flooding my basement while repeatedly banging my head against a brick wall and tearing up $100 bills. Whee!
Reply With Quote
  #10  
Old 03-20-2010, 06:00 AM
outacontrol outacontrol is offline
Member
 
Join Date: Jan 2010
Location: Stony Plain
Posts: 230
outacontrol is on a distinguished road
Default

the current on the ground wire would not in it self be dangerous, the danger occurs when the current leaves the wire or device and travels through you to ground.

the GFCI absolutely without doubt measures and compares the current in the hot/neutral (if you want to call it that) and respondes to an imbalance between the 2 wires of 6 mAmps.

here is a link: http://www.google.ca/imgres?imgurl=h...ed=0CCYQ9QEwCA

Last edited by outacontrol; 03-20-2010 at 06:06 AM.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 04:35 AM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.