![]() only problem is you can't use a grounding probe and a GFI togeather or your equipment will be always tripping. unless you have absolutly no voltage leak which.
A GFI is enough to protect you, other wise code would require us to have grounding probes in our sinks as well as close outlets haveing GFI breakers. Steve
__________________
![]() Some strive to be perfect.... I just strive. |
#3
|
|||||
|
|||||
![]() thats cuz you don't have any leakage. Grounding probes don't solve the problem they hid it, a GFI is realy all you require and if it trips you have a problem.
I split my equipment up between 4 GFI's my self I ran two heaters two MH lights and two actinic ect all set up on different GFIs. this solves the problem if one trips you don't lose everything. Steve
__________________
![]() Some strive to be perfect.... I just strive. |
#5
|
||||
|
||||
![]() Thats the purpose of the GFCI it trips before the electricity uses you as a path to ground.
|
#7
|
||||
|
||||
![]() Quote:
If the fault is in the light and the ground probe is in the tank, then it is still through you. On a side note a GFCI must trip at 0.006 Amps so I don't think 0.0059 Amps for a time of 0.0083 will be of any concern. Plus the ground probe is a lower imperdance path to ground than any other possible path for the current, and lower impedance means higher current. |