#2
|
|||||
|
|||||
![]() +1. It's too bad GFCI breakers are so expensive. But the logical workaround is to use the bathroom plugins because any downstream plug is also GFCI'd then in a way.
One thing has always confused me though. I hear 50% "this" and 50% "that", where one camp says a GFCI senses an imbalance between the hot and neutral wires, and the other camp says a GFCI senses any kind of current on the ground wire. Is it a case of "both are true" or is it a case of "the other one is an arc fault" (and if not, what is an "arc fault")? The reason I'm not convinced is because I once touched an otherwise all-powered-down light reflector (which was grounded), there was a static zap, and the GFCI tripped. (Nothing else was on at the time). So the static spark must have travelled to ground? That suggests GFCIs or at least THAT particular GFCI I was using at the time would trip on "current on ground" ? One thing about GFCI's is I get these random trips, at the rate of say once per year or so. I'm not really sure what's up with that. That's an exceedingly difficult thing to troubleshoot and diagnose because I'll go through the checklist (unplug everything, add it back one by one, using a multimeter to see if there's any current to ground) and seemingly nothing will be the chronic misbehaver. I don't know if this means the GFCI is just dodgy, or it's some kind of very infrequent fault that comes and goes, or if my checkout procedure itself is "faulty" (pun quasi-intended ![]()
__________________
-- Tony My next hobby will be flooding my basement while repeatedly banging my head against a brick wall and tearing up $100 bills. Whee! |
#3
|
|||||
|
|||||
![]() Quote:
You certainly can get nuisance tripping on GFCIs. Ceiling fans for example, on startup it will draw more current then when running. For a brief moment that inrush current will oppose a change in current between hot and ID if its a large enough difference and for a long enough period, GFCI trips. Arc fault is entirely different, its name is self explanatory, senses an arc, code says they have to be used in bedrooms... You push your bed or mattress up against the wall, bend the plug down causing an arc... That breaker will trip, without it, you potentially have a fire. The logical choice is to NOT use the a plug on the LOAD side of the bathroom receptacles, what happens when you plug your 1200watt hair dryer in? You will overload that circuit with pretty much anything else running on that same circuit... And trip the breaker... Making nuisance tripping even worse.
__________________
Do you smell that? Just waaalk away...... sloooowly |
#4
|
|||||
|
|||||
![]() I'm not sure I follow you on that last paragraph, sorry.
![]() So how come my GFCI tripped on the static discharge when nothing was on? (I touched the reflector which was grounded, there was a zot, and the GFCI tripped.) There wouldn't have been an imbalance between hot and neutral in that case?? Sorry I'm just trying to understand why it happened. Oh, one more question .. what does "ID" stand for? I know you're referring to the neutral wire in this case but I've never heard it referred to as ID before, just curious what it stands for?
__________________
-- Tony My next hobby will be flooding my basement while repeatedly banging my head against a brick wall and tearing up $100 bills. Whee! |
#5
|
|||||
|
|||||
![]() Quote:
![]() The rest well... There's a reason electrician have to go to school ![]() Referring to that wire as the neutral is INCORRECT even though everybody and their dog does, in a 2 wire system it is the identified conductor, it carries full current. In a 3 wire system its called the identified neutral, it carries the difference of current. Between the two hot conductors. Ie. Your stove is a 3 wire system... Technically called 3 wire edison. Now this is gonna get your goat, what you call the ground is actually just a bond, bonds all metal and equipment, boxes etc together. The id and the neutral are considered the grounded conductors. Inside your panel the neutral (is the neutral in the panel) is jumpered to the metal case... This jumper is the Common Grounding Conductor (if I remember correctly) then goes to earth... Or "ground". A ground fault interrupt does exactly as its name implies... A fault involving the grounded conductor (identified conductor). Static can cause tripping, so can inductive loads (motors) static is very high voltage... Even as high as 25,000 volts and very very little current, if that small amount of current introduced is high enough to trip it, it will. Remember kids, volts don't kill, current does. A gfci might trip out at 5mA, it might only take 10mA to kill you. A GFCI does not protect you from shock, it shuts the circuit fast enough that hopefully it doesn't injure you seriously, where as the circuit breaker in your panel doesn't care, its looking for the amps its rated for, you could electricy running through you all day long, as long as the total draw aint reaching what that breakers rated for. Simply won't happen with a GFCI, or atleast shouldnt
__________________
Do you smell that? Just waaalk away...... sloooowly |
#6
|
|||||
|
|||||
![]() I'll just quip in with this: while yes the gfi can protect you, it can also be a danger to your inhabitants. By that I mean, say you went on a holiday. And you had all your gear plugged into this trustful device, and pop it has a nuceince trip. Pumps are down heaters are down and your tank is toast. I say run your lighting and non mission critical systems on a gfi but keep at a min one powerhead and a heater off that gfi
__________________
"what do you mean you need another tank??" |
#7
|
|||||
|
|||||
![]() Quote:
|
#8
|
|||||
|
|||||
![]() Quote:
IMO any current that could hurt me, could hurt any fish or coral just as easily. GFCI really is a no brainer. |
#9
|
||||
|
||||
![]() Just to +1 the GFI thing. A while ago when I was building my 220, I had moved my existing 90 out of the way and off the GFI while The new tank was getting setup. While messing in the sump I had the heater glass explode IN MY HAND while live. And I mean the whole glass shield came off.
Now, that did give me quite the shock, electrically and mentally as the using was sparking and zapping as I held on to it. Since then, I always have a GFI. Thankfully the wife was standing there and the power bar it was plugged into was withing her reach ![]() Save so grief and drip loop power cords, install a GFI and don't be silly. 120V might not kill you but it will at least hurt -- a lot. |