Default Electrical Help - Stove tripping breaker *CONCLUSION*

Hey what better place to look for an electrician's advice than a forum about fish.

About 2 months ago my coil range stove would trip the electrical panel breaker if the rear large coil was turned on. We removed that coil and were cooking on three elements only but starting this week if any element is turned on it will trip the breaker, once the whole panel tripped and the house was dark. The glass fuses on the stove itself have never blown.

So we are ordering a new stove.. But I'm wondering now if the breaker or panel is suspect instead? Is there a way a novice to confirm the health of a breaker? Do they go bad?

Thanks in advance for any help given.
Keith.
__________________

Last edited by Snaz; 08-27-2009 at 03:57 AM.
Reply With Quote
  #2  
Old 08-15-2009, 11:00 PM
Starry Starry is offline
Member
 
Join Date: Dec 2005
Location: Lethbridge, AB
Posts: 619
Starry is on a distinguished road
Default

my guess is the stove had a short. if the new one still trips the breaker, replace the breaker/ breakers
__________________
Starry
180 custom starfire
http://s1083.photobucket.com/albums/...0%20july%2007/
Reply With Quote
  #3  
Old 08-15-2009, 11:33 PM
Red Coral Aquariums Red Coral Aquariums is offline
Vendor
 
Join Date: May 2008
Location: Calgary
Posts: 775
Red Coral Aquariums is on a distinguished road
Default

Quote:
Originally Posted by starry View Post
, replace the breaker/ breakers
+1
Reply With Quote
  #4  
Old 08-15-2009, 11:42 PM
subman's Avatar
subman subman is offline
Member
 
Join Date: Jan 2009
Location: Edmonton
Posts: 1,509
subman is on a distinguished road
Default

Quote:
Originally Posted by Snaz View Post
Hey what better place to look for an electrician's advice than a forum about fish.

About 2 months ago my coil range stove would trip the electrical panel breaker if the rear large coil was turned on. We removed that coil and were cooking on three elements only but starting this week if any element is turned on it will trip the breaker, once the whole panel tripped and the house was dark. The glass fuses on the stove itself have never blown.

So we are ordering a new stove.. But I'm wondering now if the breaker or panel is suspect instead? Is there a way a novice to confirm the health of a breaker? Do they go bad?

Thanks in advance for any help given.
Keith.
Breakers definitely do go bad but more often than not they don't trip. Coil burners have a tendency to short over time. I would assume that the breaker is fine but the new stove will be the proof>
__________________
225gal dt with 100g sump. Mitras, vortechs, bubble king, AI Sol and Profilux.
http://www.canreef.com/vbulletin/sho...threadid=84782
Will trade subs for frags

My other summer hobby:
http://www.edkra.ca
Reply With Quote
  #5  
Old 08-15-2009, 11:43 PM
banditpowdercoat's Avatar
banditpowdercoat banditpowdercoat is offline
Member
 
Join Date: Oct 2007
Location: 100 mile hse BC
Posts: 2,568
banditpowdercoat is on a distinguished road
Default

SOunds like the breaker is getting weak. They do not last forever. If the fuses never blew, but the breaker did. WHat's the breaker size, and whats the fuse sizes? The fuse should be smaller than the breaker, especially for just the elements. So the fuse should go first.
__________________
Dan Pesonen


Umm, a tank or 5
Reply With Quote
  #6  
Old 08-16-2009, 07:55 PM
mike31154's Avatar
mike31154 mike31154 is offline
Member
 
Join Date: Jul 2008
Location: Vernon
Posts: 2,073
mike31154 will become famous soon enough
Default

Yeah, the stove fuses not burning out and the main breaker (whole house) tripping is cause for further investigation. Have you checked the receptacle/plug for the stove itself? Could be a loose connection there causing excess current to be seen by the breaker, but not the stove. How old is your home and/or the wiring? The BC electrical code calls for the stove to be on its own circuit with no other loads, which is probably the case with your set up since it should be on at least a 40 amp breaker with two phases (3 wire cable plus ground of size 8 wire) to provide 220 VAC to the oven & probably the burners as well. A book called "Electrical Code Simplified Residential" (B.C. Book 1) published by PS Knight should be available at any home improvement center for around $12. Not a troubleshooting book per se, but plenty of good info in there on your home's electrical system. Great bang for the buck.

I'd check for loose connections before going out to buy new breakers.
__________________
Mike
77g sumpless SW
DIY 10 watt multi-chip LED build http://www.canreef.com/vbulletin/showthread.php?t=82206

Last edited by mike31154; 08-16-2009 at 08:01 PM.
Reply With Quote
  #7  
Old 08-16-2009, 08:22 PM
Snaz's Avatar
Snaz Snaz is offline
Member
 
Join Date: Aug 2008
Location: Surrey, BC
Posts: 1,034
Snaz is on a distinguished road
Default

I took the breaker out yesterday to take to the local RONA but they were closed and it wont happen tonight either. Monday

The breaker was kind of strange, it actually had three circuits on one "block".

------------------------
- 15 amp breaker
- 40 amp breaker ! The two 40 amps were joined by a common bar.
- 40 amp breaker !
- 15 amp breaker
------------------------

I have seen two 40 amps joined by common bar before, I think that is standard but I have never seen the 40 amp breakers bracketed by two 15 amp breakers. The whole thing was huge and occupies 4 slots on the panel. My tank is on one of the common 15 amp breakers but it has never tripped.

The townhouse is about 9 years old, we have had it for almost 2 years now.
__________________

Last edited by Snaz; 08-16-2009 at 08:31 PM.
Reply With Quote
  #8  
Old 08-16-2009, 08:35 PM
mike31154's Avatar
mike31154 mike31154 is offline
Member
 
Join Date: Jul 2008
Location: Vernon
Posts: 2,073
mike31154 will become famous soon enough
Default

Yep, the two 40s will be for the stove, two hot leads (black & red) with a single neutral (white) and of course ground (green or bare). Not sure why they build these monsters with 15s at either end, my 30 amp breaker for the Electric Dryer is the same idea. The reason the two 40s are tied together is that if there is a fault in either of the hot lines to the stove, both breakers will be tripped disabling all circuits to the stove. This is for safety reasons obviously. The two 15s are I guess just nice and convenient, but have nothing to do with the stove circuit.

With all 3 wire circuits, 2 hots and a neutral, the neutral needs to carry the return current for both hot wires, so you might want to double check that all connections are tight, particularly the neutral. What size is your service (main breaker) 100 amps or higher?
__________________
Mike
77g sumpless SW
DIY 10 watt multi-chip LED build http://www.canreef.com/vbulletin/showthread.php?t=82206
Reply With Quote
  #9  
Old 08-18-2009, 04:58 AM
Snaz's Avatar
Snaz Snaz is offline
Member
 
Join Date: Aug 2008
Location: Surrey, BC
Posts: 1,034
Snaz is on a distinguished road
Default

I replaced the breakers today and reseated the stove plug into the wall and still the 40 amp breakers trip as soon as they are reset or the master(100 amps) trips. Unless there is a wiring fault in the walls somewhere I have to suspect the range unit itself, a new one arrives Friday. Thanks for the advice.
Keith.
__________________

Last edited by Snaz; 08-18-2009 at 01:07 PM.
Reply With Quote
  #10  
Old 08-18-2009, 05:21 AM
hillegom hillegom is offline
Member
 
Join Date: Nov 2008
Location: Surrey
Posts: 1,985
hillegom is on a distinguished road
Default

Quote:
Originally Posted by mike31154 View Post
Yeah, the stove fuses not burning out and the main breaker (whole house) tripping is cause for further investigation. Have you checked the receptacle/plug for the stove itself? Could be a loose connection there causing excess current to be seen by the breaker, but not the stove. How old is your home and/or the wiring? The BC electrical code calls for the stove to be on its own circuit with no other loads, which is probably the case with your set up since it should be on at least a 40 amp breaker with two phases (3 wire cable plus ground of size 8 wire) to provide 220 VAC to the oven & probably the burners as well. A book called "Electrical Code Simplified Residential" (B.C. Book 1) published by PS Knight should be available at any home improvement center for around $12. Not a troubleshooting book per se, but plenty of good info in there on your home's electrical system. Great bang for the buck.

I'd check for loose connections before going out to buy new breakers.
Keith, I would try that.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 03:44 AM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.