ok...retract my comment...I was going somewhere else with this on a residential note.
Reply With Quote
  #22  
Old 10-16-2008, 07:04 PM
kaboom kaboom is offline
Member
 
Join Date: Mar 2006
Location: Calgary
Posts: 204
kaboom is on a distinguished road
Default

Thanks for the link AJ77, toxic's numbers make alot more sense now. I need to evaluate my joist spans and figure out a way to add columms underneath.
Reply With Quote
  #23  
Old 10-17-2008, 12:28 AM
Dale's Avatar
Dale Dale is offline
Member
 
Join Date: Jun 2006
Location: Abbotsford, BC.
Posts: 189
Dale is on a distinguished road
Default

I have a 140 G. on the second floor positioned over the cantilever outset for a china cabinet in the dining room. It hasn't shifted in the three years or so that it's been there. Placing the tank against the wall with the joists running perpendicular to it like this:

t a n k

j
o
i
s
t

is the strongest position it can be in and I have seen many large tanks on second floors that way without additional support.

Toxic, your 40lb/15lb per sq ft idea just clouds the issue. It doesn't relate to placing a load in one area of the room. What it relates to is the total weight the room (floor) can bear.
For ex. A 10' x 10' room can hold 15lb's/sq. ft. DW min. 10x10x15=1500. The room can hold 1500lb's DW.
The formula can't be used to work out how much a specific part of the room can hold.

Last edited by Dale; 10-17-2008 at 12:48 AM.
Reply With Quote
  #24  
Old 10-17-2008, 01:05 AM
JDigital's Avatar
JDigital JDigital is offline
Member
 
Join Date: May 2008
Location: Airdrie
Posts: 2,795
JDigital is on a distinguished road
Send a message via MSN to JDigital
Default

Quote:
Originally Posted by Snappy View Post
I am over 200 lbs and have never had a fear of falling through my floor.
LMAO.... someday Greg! someday, when you least expect it...
__________________
180G Office Reef. Started Sept 2012 http://www.canreef.com/vbulletin/showthread.php?t=88894

62G Starfire Reef. Started Jan 2013 http://www.canreef.com/vbulletin/showthread.php?t=89988
Reply With Quote
  #25  
Old 10-17-2008, 01:27 AM
Jay180reef's Avatar
Jay180reef Jay180reef is offline
Member
 
Join Date: Sep 2008
Location: Calgary
Posts: 139
Jay180reef is on a distinguished road
Default

I've got a 180 gal 72x24x24 above my garage as well, I put a telepost under the joist under my tank. It was around $70 at HD. I put it in right before adding water to my tank. No problems at all, great for peace of mind.
Reply With Quote
  #26  
Old 10-17-2008, 01:50 AM
toxic111 toxic111 is offline
Member
 
Join Date: Mar 2008
Location: Lloydminster, SK
Posts: 237
toxic111 is on a distinguished road
Default

Quote:
Originally Posted by Dale View Post
I have a 140 G. on the second floor positioned over the cantilever outset for a china cabinet in the dining room. It hasn't shifted in the three years or so that it's been there. Placing the tank against the wall with the joists running perpendicular to it like this:

t a n k

j
o
i
s
t

is the strongest position it can be in and I have seen many large tanks on second floors that way without additional support.

Toxic, your 40lb/15lb per sq ft idea just clouds the issue. It doesn't relate to placing a load in one area of the room. What it relates to is the total weight the room (floor) can bear.
For ex. A 10' x 10' room can hold 15lb's/sq. ft. DW min. 10x10x15=1500. The room can hold 1500lb's DW.
The formula can't be used to work out how much a specific part of the room can hold.

This is just the Building Code design criteria, shorter spans may hold more load. Remember dead load of 15lbs/ft2 is based on the weight of material only, not anything else.

I stand by my comment that 2500lbs over 12ft2 is serious overloading a floor based on the building code. Better be safe than sorry.

Again with out looking at the floor I can't say what it can hold exactly, and that is the reason for an engineer. It has been awhile since I have done the calculations.

Oh, and jsut beacuse your floor has not moved in 3 years that you can see does not mean there are no problems. I have seen enough over my 20+ years of experience in design & construction to say be careful.
Reply With Quote
  #27  
Old 10-18-2008, 05:10 AM
Dale's Avatar
Dale Dale is offline
Member
 
Join Date: Jun 2006
Location: Abbotsford, BC.
Posts: 189
Dale is on a distinguished road
Default

I'm not worried

T, I wasn't questioning your experience, just noting that the numbers didn't equate to the specific problem. There isn't anything wrong with being careful and if it is easy and gives piece of mind to beef things up then it's all good but this type of question arises fairly regularily and for most tanks of that size there is no problem.
I can't recall the last time I've heard of a floor collapsing because of a non custom aquarium actually. I'm sure it has happened somewhere but if it was that close a call I'm sure there would be more incidents.

This week I have serviced a 230G., 300G., 150G., 140G. and a 135G. tanks; all on joisted floors - no collapses so far.
Reply With Quote
  #28  
Old 10-18-2008, 07:45 AM
kaboom kaboom is offline
Member
 
Join Date: Mar 2006
Location: Calgary
Posts: 204
kaboom is on a distinguished road
Default

After having a closer look at my floor, I realize the joists run parallel to the proposed tank placement. This could be a problem right? Let me refresh the scenario again. Tank is situated along a load barring wall above the garage where there is a supporting joist and beam that lines up right in the middle of the tank position. The floor joists however runs parallel with the tank. The optional teleposts is no longer an option. I am now considering a 125g tank instead of the 180g first thought. Without additional support, can I just wing it with a 125g.
Reply With Quote
  #29  
Old 10-18-2008, 03:30 PM
mark's Avatar
mark mark is offline
Member
 
Join Date: Nov 2002
Location: Edmonton AB
Posts: 4,212
mark is on a distinguished road
Default

Since you're worried, get that engineering report, (might PM GreenSpottedPuffer if he'll give you an idea of cost, since he had it done) and figure how to stay big or you'll be kicking yourself later that you didn't.

Can you double up the first joist, expensive but install a steel beam?
Reply With Quote
  #30  
Old 10-18-2008, 04:11 PM
Sam1969 Sam1969 is offline
Member
 
Join Date: Apr 2007
Location: Edmonton
Posts: 73
Sam1969 is on a distinguished road
Default

Not sure how much room you have in your garage, but if it were me I would build a supporting wall in your garage directly below your tank. Make it floor to floor 12 inch centers with construction grade 2 x 6 and tie it in to the existing joist. If your anything like me you can always use more shelving in your garage ....
__________________
Starting fresh ... 90 gal, 40gal sump, sundial T5HO x 4, 2 x koralia 2's, ASM G1X skimmer
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 03:00 AM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.