#19
|
|||||
|
|||||
![]() The Apex Reference Manual is full of little gems! Remember my questioning of a logged current spike of 75 amps?
https://www.neptunesystems.com/downl...nce_Manual.pdf Page 139 "EB8 or EB4 shows incorrect amperage Similar to the previous issue, the EBx may need recalibration. The process is simple but you must be comfortable knowing how to telnet into your controller. If so, then read on. 1. Identify the Aquabus number of the EB8 or EB4 that you want to calibrate. If your EBx is numbered EB8_3 then the Aquabus number is 3. 2. Unplug everything from the EBx or at least make 100% certain it’s all turned off. This is critical. Whatever amperage the EBx is pulling when the calibration is run becomes the new zero point. You want to make sure it’s pulling 0. 3. Telnet into the controller and login with your userid and password. 4. Issue the following command: eb8zero n where ‘n’ is the Aquabus number of the EBx you want to calibrate. If you’re calibrating an EB4, the command is still ‘eb8zero’. So using the above example of an EB that is known as ‘EB8_3’ the command would be ‘eb8zero 3’. This command is case sensitive and should be entered in lower case as is shown. It executes immediately and there’s no confirmation or message when finished, just a new telnet prompt. 5. Quit telnet. That’s it. Your EBx should now read the proper amperage load when devices are active."
__________________
Mike 77g sumpless SW DIY 10 watt multi-chip LED build ![]() |