Default Any HVAC experts?

So I have a question about my air exchanger. When we initially built the house, they told us they installed an air exchanger as these new houses are somewhat air tight. They said to be careful how much I use it as it could increase my electric bill if I keep blowing all my hot air outside and my furnace has to run more often to keep the house at a certain temperature. Anyways, years later we had a A/C unit installed and connected to the furnace. We still hadn't really used the air exchanger up to this point. I recently turned on the air exchanger while my furnace thermostat was set to off just to circulate the air in my house. I noticed that the fan on my A/C unit would run when the air exchanger was on. It was not cooling the air but it was running continuously while the air exchanger was on. Is this normal? I don't know much about these things.
Reply With Quote
  #2  
Old 04-25-2012, 03:00 PM
rayjay rayjay is offline
Member
 
Join Date: Dec 2002
Location: London, Ontario
Posts: 340
rayjay is on a distinguished road
Default

Depends on a few things. First, if it is JUST an air exchanger then yes, you have to reheat the incoming air (or cool it). If it is an HRV then those units recover much of the heat (cold) so that only a portion has to be reheated or cooled.
Most exchangers now are plumbed to the furnace to give distribution throughout the house so the fan will come on for that distribution.
My HRV is installed so that it can go throughout the house or only in the basement where all my tanks and cultures are, but I have to physically change the HRV output to just the basement or to connect it to the cold air return of the furnace.
Reply With Quote
  #3  
Old 04-25-2012, 03:03 PM
The Guy The Guy is offline
busy with fresh water.
 
Join Date: Dec 2011
Location: Kelowna, BC
Posts: 1,041
The Guy is on a distinguished road
Default

Quote:
Originally Posted by Seriak View Post
So I have a question about my air exchanger. When we initially built the house, they told us they installed an air exchanger as these new houses are somewhat air tight. They said to be careful how much I use it as it could increase my electric bill if I keep blowing all my hot air outside and my furnace has to run more often to keep the house at a certain temperature. Anyways, years later we had a A/C unit installed and connected to the furnace. We still hadn't really used the air exchanger up to this point. I recently turned on the air exchanger while my furnace thermostat was set to off just to circulate the air in my house. I noticed that the fan on my A/C unit would run when the air exchanger was on. It was not cooling the air but it was running continuously while the air exchanger was on. Is this normal? I don't know much about these things.
Yes if you are running the air exchanger the furnace fan will come to replace the air in the house that the exchanger is removing from the house. Air going out has to be replaced with air from your furnace it will have a fresh air outside connection that pulls in the fresh air to accomplish this. This is a typical hook up in the newer homes.
__________________
Hey! I never "LEFT" the hobby, just doing fresh water now. Which is still listed as part of Canreef if I'm not mistaken.
Reply With Quote
  #4  
Old 04-25-2012, 03:06 PM
sphelps's Avatar
sphelps sphelps is offline
Member
 
Join Date: May 2006
Location: Lyalta, East of Calgary
Posts: 4,777
sphelps is on a distinguished road
Default

Depends on how it's setup, quite often if you have forced air heating the air exchanger ties into the cold air return and heating ducts of the furnace. If this is the case the furnace fan needs needs to run with the exchanger fan. I'm not sure about the AC fan, central air units have a fan on the unit placed outside and the coil is just placed in the furnace and uses the furnace fan. So which fan is on exactly?
Reply With Quote
  #5  
Old 04-25-2012, 03:06 PM
Seriak's Avatar
Seriak Seriak is offline
Member
 
Join Date: Jun 2002
Location: Calgary
Posts: 954
Seriak is on a distinguished road
Default

But should my air conitioning unit fan come on as well. I am okay with the furnace fan being on. Would that mean I cannot run my air exchanger in winter as my air conditioning unit would be covered and I am assuming you shouldn't have the fan running under the cover.
Reply With Quote
  #6  
Old 04-25-2012, 05:38 PM
cwatkins's Avatar
cwatkins cwatkins is offline
Member
 
Join Date: Oct 2009
Location: Cloverdale, BC
Posts: 352
cwatkins is on a distinguished road
Default

I don't think the fan on the outdoor A/C condensing unit should be running...

If it's running, it probably means the compressor is running as well, which means your A/C is effectively ON.
__________________
Tank Journal Thread
Reply With Quote
  #7  
Old 04-25-2012, 05:45 PM
Seriak's Avatar
Seriak Seriak is offline
Member
 
Join Date: Jun 2002
Location: Calgary
Posts: 954
Seriak is on a distinguished road
Default

Quote:
Originally Posted by cwatkins View Post
I don't think the fan on the outdoor A/C condensing unit should be running...

If it's running, it probably means the compressor is running as well, which means your A/C is effectively ON.
That is what I thought, but when I went to the registers it was blowing warm air not cold air and the thermostat was set to off. As soon as I turned off the air exchanger the fan stopped turning on the a/c unit. Since then I have had the a/c on and it blows cold air just fine. I am at a loss. Maybe I will go turn the thermostat to heat and see if the air exchanger still turns on the a/c unit.
Reply With Quote
  #8  
Old 04-25-2012, 06:30 PM
Delphinus's Avatar
Delphinus Delphinus is offline
Member
 
Join Date: Dec 2001
Location: Calgary
Posts: 12,896
Delphinus has a spectacular aura aboutDelphinus has a spectacular aura aboutDelphinus has a spectacular aura about
Send a message via MSN to Delphinus
Default

That seems really weird to me - can you call the place that did the installation?
__________________
-- Tony
My next hobby will be flooding my basement while repeatedly banging my head against a brick wall and tearing up $100 bills. Whee!
Reply With Quote
  #9  
Old 04-25-2012, 07:08 PM
Seriak's Avatar
Seriak Seriak is offline
Member
 
Join Date: Jun 2002
Location: Calgary
Posts: 954
Seriak is on a distinguished road
Default

Quote:
Originally Posted by Delphinus View Post
That seems really weird to me - can you call the place that did the installation?
Unfortunately, they were not that great to deal with in the first place and it was so many years ago they wouldn't do it for free now. I just talked to an electrician friend and he suggested that if everything else works fine, he would just turn off the breaker for the air conditioner in the winter and not worry about it although it did sound to him as if they wired something wrong.
Reply With Quote
  #10  
Old 04-25-2012, 07:14 PM
subman's Avatar
subman subman is offline
Member
 
Join Date: Jan 2009
Location: Edmonton
Posts: 1,509
subman is on a distinguished road
Default

I had something like this in my last house. When we turned on the circulating fan the AC compressor would start. I was told it had to do with the relays for the fans and they would need to be changed. I never did, I just tuned the breaker of for the AC off.
__________________
225gal dt with 100g sump. Mitras, vortechs, bubble king, AI Sol and Profilux.
http://www.canreef.com/vbulletin/sho...threadid=84782
Will trade subs for frags

My other summer hobby:
http://www.edkra.ca
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 11:05 PM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.