Default Electrical "Leakage" in a tank??

I don't know how to better describe the situation, but I was just planning on heading out and I put my hand in my tank to do something or other, and I had a few cuts on my fingers, well - it hurt like the DICKENS

I couldn't for the life of me figure out why, I tried it with other fingers that had cuts, and the same pain. I tested a few other things out, and then I got the same feeling on my OTHER fingers, with no cuts. Pulling the plug to everything made me realize that it was something electrical.

I proceeded to unplug everything, one by one, and I cleaned out some much needing cleaned powerheads, and made sure nnothing was being blocked or running "dry" - I did notice that a few of my PH's in my sump were in rough shape, and I think my pump to the UV unit was fully plugged.

Needless to say, all is done and it's fine now, no "zapping" when putting my fingers in my tank, and all livestock seems okay (might explain why my SPS have fully browned and dying) - and it had nothing to do with my heater, that one never "zapped" when it was the only thing plugged in, and that was one of the first things I tried.

But is there anything else I should worry about? I have a grounding cable on my tank to suck away the excess, I can't imagine what this would have been like without that. Anyone experience this, suggestions, what I should be aware of or watch out for?

Thanks!
Reply With Quote
  #2  
Old 06-17-2007, 11:53 PM
andsoitgoes's Avatar
andsoitgoes andsoitgoes is offline
Member
 
Join Date: Sep 2006
Location: Secret Location
Posts: 433
andsoitgoes is on a distinguished road
Default

Well, things are not really any better, I have figured out why it was intermittent, though!

I have a spot on the floor that some water spilled on, it's carpet so it holds that water nicely.

when I stand on that and put my hand in tank, zap. Dry, it's fine.

What's going on, what do I do? It's owie and I don't want to kill my tank!
Reply With Quote
  #3  
Old 06-17-2007, 11:56 PM
0sprey's Avatar
0sprey 0sprey is offline
Member
 
Join Date: May 2007
Location: Okotoks
Posts: 71
0sprey is on a distinguished road
Default

You should install a GFI (Ground Fault Interrupter) on your plug. It's quick and easy to do. When anything starts leaking electricity into the water the GFI will trip and break the circuit. You'll have to unplug everything and plug them back in one at a time to see which appliance is leaking current. Then you can replace the offender.
Reply With Quote
  #4  
Old 06-18-2007, 12:05 AM
andsoitgoes's Avatar
andsoitgoes andsoitgoes is offline
Member
 
Join Date: Sep 2006
Location: Secret Location
Posts: 433
andsoitgoes is on a distinguished road
Default

That might be an idea, was hoping for reassurance and a warm fuzzy response that all is fine and it's normal

Don't know when I'll be able to actually get a gfic or install it, I know they're easy... But it's just a matter of getting out and getting

Ugh, frustrating. How dangerous is a small shock like this?
Reply With Quote
  #5  
Old 06-18-2007, 12:33 AM
Static Static is offline
Member
 
Join Date: Jun 2005
Location: Victoria
Posts: 103
Static is on a distinguished road
Send a message via MSN to Static
Default

A few articles I've read lately http://reefkeeping.com/issues/2005-06/sp/index.php as an example suggest that grounding probes cause more current flow in the tank, even if the voltage reading seems lower.

If you put a voltmeter on either terminal on a battery that's not hooked up you will read voltage, if you connect the two terminals, ie short circuit them you will read less or no voltage on your voltmeter. What is suggested instead is to find the peice of faulty equiptement and replace it rather than providing a rout for the "stray voltage" to escape.
Reply With Quote
  #6  
Old 06-18-2007, 01:31 AM
mark's Avatar
mark mark is offline
Member
 
Join Date: Nov 2002
Location: Edmonton AB
Posts: 4,212
mark is on a distinguished road
Default

It doesn't take much current to kill (fractions of an amp) and getting a tingle isn't normal.

Should get a GFI and a ground probe as you found all can basically look normal but still have the potential to cause harm. That way in the future when something does start to fail the indicator will be the GFI tripping rather than you flopping on the floor.

To find the device causing the problem, suggest with a GFI and ground probe, unplug everything, then start plugging back in one at a time. What trips will be the device that's leaking the current.

As for the argument that what if I'm away and the GFI trips and the tank crashes. Well, in my case believe (at least pretty sure) the wife would rather the tank crash than me dead.

I've got multi GFI circuits with the idea if I get something like a little salt creep on the lights, it won't take out all the pumps, if the sump return fails, the CL is on another etc.
Reply With Quote
  #7  
Old 06-18-2007, 03:46 AM
deep6er deep6er is offline
Member
 
Join Date: Aug 2005
Location: Richmond
Posts: 196
deep6er is on a distinguished road
Default

I had this problem a long time ago too. . Trying to find what was causing the short was very painfull. And it just so happened that it was the last one i checked. It was my CL skimmer. My suggestion to you is to find what is causing it.
__________________
Time wasted is existence; used is life.
Reply With Quote
  #8  
Old 06-18-2007, 04:09 AM
Static Static is offline
Member
 
Join Date: Jun 2005
Location: Victoria
Posts: 103
Static is on a distinguished road
Send a message via MSN to Static
Default

You can use a voltmeter to test your equipment. One probe in the tank, and the other in the ground of your wall socket. Simply unplug each piece of equipment until you see 0 volts.
Reply With Quote
  #9  
Old 06-18-2007, 04:58 AM
andsoitgoes's Avatar
andsoitgoes andsoitgoes is offline
Member
 
Join Date: Sep 2006
Location: Secret Location
Posts: 433
andsoitgoes is on a distinguished road
Default

Having ANYTHING plugged in will cause the voltage to go up, even an incremental amount. I found a few good articles on that here:

http://www.reefs.org/library/aquariu...996/996_5.html

however - the biggest factor is that the ONLY time I feel it is when I stand on the "wet spot" on the floor. I move off of that, and nothing.

I had the + wire of the voltmeter in the tank, I took the ground and stood on the spot, the needle moved to a VERY small amount, but it moved. I took my foot off that spot, and all was hunky dory.

How does this make sense?
Reply With Quote
  #10  
Old 06-18-2007, 05:17 AM
Static Static is offline
Member
 
Join Date: Jun 2005
Location: Victoria
Posts: 103
Static is on a distinguished road
Send a message via MSN to Static
Default

It makes sense because the dry spots on your floor are better insulators than the wet spots. Voltage is the difference of electrons between 2 parts of a circuit. In this case you are making yourself and the wet spot on the floor part of the circuit. When you move off the wet spot you are opening the circuit, like flipping a switch. In other words, when you are standing on dry ground you are no longer grounded, and the voltage is not attracted to you. Is it a wood floor under the carpet or concrete?

Did you check the voltage between the tank water and the ground on your electrical outlet? You should just be able to touch the voltmeter probe to the screw that holds the faceplate onto your outlet.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 06:01 PM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.