Canreef Aquatics Bulletin Board  

Go Back   Canreef Aquatics Bulletin Board > Other > Lounge

 
 
Thread Tools Display Modes
Prev Previous Post   Next Post Next
  #29  
Old 04-30-2012, 01:44 PM
Seriak's Avatar
Seriak Seriak is offline
Member
 
Join Date: Jun 2002
Location: Calgary
Posts: 954
Seriak is on a distinguished road
Default

Quote:
Originally Posted by weyburnt View Post
Yes this would make sence except he said this still happens when the t stat is switched off. Also I don't think most t stats jumper the y and g when in auto. I'm pretty sure the furnace board takes care of this. Or else when the fan switch was in off, and the t stat was in cool, the fan would not run. Sometimes on older furnaces without a y point people will jumper these points but op said thier was no jumper. The r and the rh need to be jumpered out unless you have a system with separate heating and cooling transformers. Which you don't. If the unit does not do this with the t stat wire disconnected at the bored then double check the t stat wiring and replace the t stat. I do not believe a relay is the way to go. I Hooked 2 of these up last week alone. The only way you should need a relay is if it is an older furnace with no y point.
Which wire do you want me to disconnect from the tstat or do you want me to disconnect them all?
Reply With Quote
 


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 09:12 PM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.