Quote:
Originally Posted by weyburnt View Post
Yes this would make sence except he said this still happens when the t stat is switched off. Also I don't think most t stats jumper the y and g when in auto. I'm pretty sure the furnace board takes care of this. Or else when the fan switch was in off, and the t stat was in cool, the fan would not run. Sometimes on older furnaces without a y point people will jumper these points but op said thier was no jumper. The r and the rh need to be jumpered out unless you have a system with separate heating and cooling transformers. Which you don't. If the unit does not do this with the t stat wire disconnected at the bored then double check the t stat wiring and replace the t stat. I do not believe a relay is the way to go. I Hooked 2 of these up last week alone. The only way you should need a relay is if it is an older furnace with no y point.
Which wire do you want me to disconnect from the tstat or do you want me to disconnect them all?