Default Finally

I finally figured this out
I have all of my Switches set to Open ( as in no contact ) when they rise, so keep this in mind when setting up yours

Only 1 Alarm can be assigned per Channel, so I set up Alarms in myReef as follows;

Alarm 1 is the Overflow high float
-Device 1 is SWA - Trigger 0.5 - Above - Logic OR ( doesn't matter with only one device )

Alarm 2 is the Sump low float
-Device 1 is SWB - Trigger 0.5 - Above - Logic OR ( doesn't matter with only one device )

Alarm 3 is Both
-Device 1 is SWA - Trigger 0.5 - Above - Logic OR ( OR means it will trip on either device )
-Device 2 is SWB - Trigger 0.5 - Above - Logic OR ( AND means it needs both devices to trip )

Now I have the programming I needed, and my Return pump is still a Pump, not a Switch

For those of you using myReef to do this;
A Trigger value of 0.5 and set to Above will trip when Open ( no contact )
A Trigger value of 0.5 and set to Below will trip when Closed ( contact )

If you're using your Head Unit to do this, it will give you the option to select the word trip and so on.